2,500 kW Liquid-to-Liquid In-Row CDU image number 0
2,500 kW Liquid-to-Liquid In-Row CDU image number 1
2,500 kW Liquid-to-Liquid In-Row CDU image number 2
2,500 kW Liquid-to-Liquid In-Row CDU image number 3
Unfold the Power of Water
The Cooler Master 2,500 kW Liquid-to-Liquid In-Row Coolant Distribution Unit (CDU) manages a 2,500-kW heat load. The CDU effectively segregates the primary and secondary loops using one brazed plate heat exchanger (BPHE). This enables high-capacity liquid cooling in data centers, providing significantly higher power and compute density. The high-efficiency heat exchanger can produce an approach temperature difference (ATD) of 5 degrees Celsius with 2,500 kW heat dissipation.
Features
  • Efficiently cools up to 2,500 kW.
  • Supports facility water supply temperatures from 2°C to 45°C (ASHRAE W2–W4 Liquid Cooling Class).
  • Maximum secondary flow rate: 4,200 LPM.
  • 46U in-row chassis.
  • Stainless-steel, gasket-less, brazed heat exchanger rated to 19 bars.
  • Sanitary flanges and clamps for easy connections.
  • Redfish API for remote management and monitoring.
  • Optional Multi-Machine Linkage for centralized coordination of multiple units.
  • 10.1-inch touchscreen with real-time monitoring.
  • Menu-driven interface for status, diagnostics, and configuration.
  • Monitors water quality with pH, ORP, conductivity, turbidity, and humidity sensors.
2,500 kW CDU CONTROL PANEL INTERFACE
Benefits
  • Supports high heat loads with low power consumption (approximately 40 kW).
  • Offers standardized remote access and control.
  • Features a large, intuitive interface for easy operation.
  • Manages condensation by diverting low-temperature primary supply fluid to the return.
  • Keeps facility and IT equipment water separate, allowing different fluids in the secondary loop for specific needs.
  • Provides comprehensive secondary loop control and monitoring for optimal IT cooling.
  • Centralized management enables automatic failover and coordinated operation across units, improving energy efficiency and reliability while reducing complexity.
  • Delivers real-time alarm monitoring for complete system and environmental protection.
  • Enables early leak detection to prevent damage and flooding.
  • Streamlined menu system minimizes training time and simplifies maintenance.
MAXIMIZED COOLING WITH PRECISION
The Cooler Master 2,500 kW CDU is equipped with sensors to monitor various fluid conditions, including flow, pressure, pH, ORP, electrical conductivity, temperature, humidity, and leakage. This allows for precise tracking and supports proactive maintenance and error detection through its integrated alarm system. Cooler Master's liquid cooling technology is designed for both new and existing data centers, helping managers address the demands of high-performance computing and AI. These solutions enhance performance, energy efficiency, and sustainability, while also reducing operational costs.
Performance
Maximum Cooling Capacity
2,500 kW @ 5°C ATD, 3750 LPM
Nominal Cooling Capacity/Range
1,500 kW @ 4°C ATD, 2250 LPM
Approach Temperature Difference (ATD)
3.6 to 5.6°C
Primary Side
Primary Pressure Drop
3,250 LPM @ 26 psi (470-micron-filtered water)
Maximum Operating Pressure
150 psi
Sensors
Flow Rate, Pressure (Inlet/Outlet, Filter), Inlet/Outlet Temperature
Filtration
870-micron Mesh #20 / 470-micron Mesh #35
Secondary Side
Flow Rate
1,300 to 4,200 LPM (343 to 1109 GPM) at 52 to 75 psi
Sensors
Flow Rate, Pressure (Secondary Inlet/Outlet, Filter Inlet/Outlet), Inlet/Outlet Temperature, pH, Conductivity, Coolant Level (Tank, Secondary Inlet, Pump Inlet), Oxidation Reduction Potential (ORP), Turbidity
Filtration
25-micron or 50-micron
Pump Module
2 x Pumps, 1+1 Redundancy
Power / Electrical
Input Voltage
380 to 480 V AC, 50/60 Hz
Rated Current
67.5 A
Power Consumption
40 kW
Wiring
3-Phase 5-Wire System
Power Supply Unit
2 x Power Supply Units
UPS
Yes (Control System)
ATS
Yes
Communications
Group Control
Up to 32 Units
Communication, Protocol, Remote Access
Ethernet, RS-485 Modbus Communication, 4-20 mA Analog current communication / Modbus TCP, TCP/IP, Redfish
Protections
Alarms
Liquid Level, Liquid Leakage, High/Low Pressure, High/Low Flow Rate, High Ambient Temperature, High/Low Conductivity Value, High/Low Humidity Value, High/Low pH Levels, High/Low coolant Temperature, Communication Failure Alerts
Protections
Over-Current, Over-Voltage, Grounding, Internal Leak Detection